[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Simple Transient Model
Betsy
You say below you are using a rather low surface convection coefficient
of 1.0 W/m2-K. The overall surface conductivity from air to air
includes this coefficient and yours will introduce a lot of thermal
resistance. It sounds like you want to use a much higher value -- like
maybe 1000.0 W/m2-K
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Elizabeth
Ricker
Sent: Tuesday, December 05, 2006 7:37 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Simple Transient Model
Mike,
I took a look at the files for the ASHREA documentation, but that did
not solve my problem. The primary issue is that I am trying to examine
the temperature response in a system with NO thermal mass (i.e. the
walls, floor, and roof all have very low densities ~.0001 and Cp values
~.0001). The only thermal mass that should be present is in the air
within the room. Given these conditions I should be seeing a response
that is very fast in letting the air in the room cool from 26C to the
outdoor temperature of 0C. What I am actually seeing is a response on
the order of 35 hours for air to cool with all walls adiabatic except
for a single conducting wall. I am currently setting my adiabatic walls
by giving them very low conductivites. Is there an alternative way of
defining adabatic walls with no thermal mass? Any ideas on why the
response time would be so long? Are there any other forms of thermal
mass other than the air that might be residual in the simulation and
giving me longer time constants than expected?
Thank you for your help,
Betsy
"Michael J. Witte" <mjwitte@xxxxxxxx <mailto:mjwitte%40gard.com> >
wrote:
It is hard to say what the problem may be. Did you zero out all of the
solar
in the weather file, or set all of the surfaces to "NoSun"?
A similar test is reported in "EnergyPlus Testing with ASHRAE 1052-RP
Toolkit -
Building Fabric Analytical Tests". Perhaps comparing your test inputs
and
results with tests TC1-TC3 will help you find the problem. This report
is
available at:
http://www.eere.energy.gov/buildings/energyplus/testing.html
<http://www.eere.energy.gov/buildings/energyplus/testing.html>
Follow the link for "ASHRAE Research Project 1052"
Mike
On 2 Dec 2006 at 17:49, elizabeth.ricker wrote:
> Hi All,
> I am currently looking at a simple transient model in
> EnergyPlus. I would like to heat a room (1 zone) to 26C for a
> period, then allow it to cool to the outdoor temperature (0C) and
> analyze the time response of the system. I am looking at the
> reponse given that heat is only leaving through one wall, there is
> no thermal mass in that wall, and the remainder of the walls are
> super insulating. The convection coefficients on each wall are set
> to 1 W/m2K and the conductivity of the single conducting wall is
> very high (k = 1000, L = .1). Given these conditions the only
> thermal mass in my model should be that of the air in the room.
> Also, I am running a modified weather file with T = 26C for the
> first month, and then going to 0C for the remainder of the year. The
> results that I am showing are presenting a much longer time reponse
> than I would expect, and do not necessarily show an exponential time
> decay. Any suggestions on what might be going wrong in my model?
>
> Thank you,
>
> Betsy Ricker
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov <http://www.energyplus.gov>
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
<http://groups.yahoo.com/group/EnergyPlus_Support/>
>
> Attachments are not allowed -- please post any files to the
appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and
press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx <mailto:EnergyPlus-Support%40gard.com>
---------------------------------
Any questions? Get answers on any topic at Yahoo! Answers. Try it now.
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/