No.  The baseboard heater in EnergyPlus is programmed as a heating device.

Mike


On 12 Dec 2006 at 10:09, Simon Rees wrote:

> Are the chilled beams in question passive or active? Passive chilled
> beams are physically very similar to baseboard heaters - pipes with fins
> that work by natural convection. I will need to  model a passive chilled
> beam system shortly and wondered if the baseboard heater model could be
> used. Would the model work in cooling mode?
> Thanks, Simon
> 
> -----Original Message-----
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Fred Buhl
> Sent: 11 December 2006 22:45
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: Re: [EnergyPlus_Support] Re: Chilled beam modeling
> 
> 
> That's a good choice.
> 
> Fred Buhl
> 
> miaoworld wrote:
> > I agree with Phil that the chiled beam system is predominantly 
> > convective especially when the system is active chilled beam system.
> >
> > How about the 4-pipe induction system in the energyplus?
> >
> > Miao.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> > <mjwitte@...> wrote:
> >   
> >> There are no chilled beam examples.  It has been suggested that
> >>     
> > chilled beam
> >   
> >> systems can be modeled using the low temperature radiant system (with
> 
> >> chilled water in the slabs) and then manually increase the convection
> 
> >> coefficient on the ceiling surfaces (using the CONVECTION 
> >> COEFFICIENTS object).  For an example of radiant slab cooling
> >>     
> > systems, see
> >   
> >> ExampleFiles\RadLoHydrHeatCoolAuto.idf
> >>
> >> Mike
> >>
> >>
> >> On 1 Dec 2006 at 20:36, miaoworld wrote:
> >>
> >>     
> >>> Currently I am trying to model the chilled beam system with
> >>> Energyplus.  Did anyone has any examples or suggestions?  Any 
> >>> information would be appreciated. 
> >>>
> >>> Thanks
> >>>
> >>> Miao.
> >>>
> >>>
> >>>
> >>> The primary EnergyPlus web site is found at: 
> >>> http://www.energyplus.gov
> >>>
> >>> The group web site is: 
> >>> http://groups.yahoo.com/group/EnergyPlus_Support/
> >>>
> >>> Attachments are not allowed -- please post any files to the
> >>>       
> > appropriate folder
> >   
> >>> in the Files area of the Support Web Site.
> >>>
> >>> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf
> >>>       
> > and press the
> >   
> >>> "search" button.
> >>>  
> >>> Yahoo! Groups Links
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>       
> >> ========================================================
> >> Michael J. Witte, GARD Analytics, Inc.
> >> EnergyPlus Testing and Support      
> >> EnergyPlus-Support@...
> >>
> >>     
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at: http://www.energyplus.gov
> >
> > The group web site is: 
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the 
> > appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and 
> > press the "search" button.
> >  
> > Yahoo! Groups Links
> >
> >
> >
> >   
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at: http://www.energyplus.gov
> 
> The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and
> press the "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/