[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: The question about the internal thermal m ass



Mike,

For the third question, if there is no geometric position in the 
zone, then how is the radiation with other surfaces able to be 
considered(and further the solar radiation)? I feel this calulation 
could be related to the object's place.

Eric

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@...> wrote:
>
> 1.  No, the air volume is not adjusted.  If you want to reduce the 
capacitance 
> of the zone air, change the volume in the ZONE object.  But the 
contribution of 
> air mass is very tiny compared to the thermal mass of surfaces, so 
this should 
> produce negligible changes in results.
> 
> 2.  The only limit on internal mass area is that the radiant heat 
transfer 
> calculations require that any one surface must have an area less 
than or equal 
> to the sum of all other surfaces in the same zone.  You can have 
multiple 
> internal mass objects in the same zone.
> 
> 3.  In your intial post, you stated "I know this thermal mass only 
consider the 
> convection heat transfer with zone air."  This is incorrect.  
Internal mass 
> surfaces participate fully in all zone heat transfer mechanisms, 
including 
> convection with the zone air, thermal radiant (receiving radiant 
internal gains 
> and exchanging with other surfaces), and solar gains (diffuse, and 
direct if 
> the solar distribution is set to MinimalShadowing).  It is just 
like a regular 
> heat transfer surface except that is has no geometric position in 
the zone.  
> 
> Mike
> 
> 
> On 30 Jan 2007 at 8:35, wanglei wrote:
> 
> > 
> > Dear Linda
> >    Thank you very much for your reply.
> > I have two question about the internal mass.
> > 1.  If I add a thermal mass in a zone , the volume of the air is 
subtract by this thermal mass
> > 2. what is the maximum thermal mass area, which I can input to 
the area field.  
> > Thank you ,verymuch!
> > 
> > 
> > 
> > 
> > From: "Linda Lawrie" <linda@...>
> > To: energyplus_support@xxxxxxxxxxxxxxx
> > Date: Mon, 29 Jan 2007 23:04:22 +0800 (CST)
> > Subject: Re: [EnergyPlus_Support] The question about the 
internal thermal m ass
> > 
> > 
> > 
> > 
> > 
> > Remember that the internal mass will absorb heat and retain that 
> > temperature. "when I increasing the area of thermal mass above 
50, <BR>the average temperature is high than less thermal mass. I 
think there <BR>is some problem." -- I would be looking at the 
significance of area 
> > "50" is with the rest of your zone.
> > 
> > A more definitive answer will come if you upload your input file 
to 
> > the support group area.
> > 
> > Linda
> > 
> > EnergyPlus WebSite: http://www.energyplus.gov
> > Owner: EnergyPlus_Support list
> > Member: EnergyPlus Development Team
> > 
> > [Non-text portions of this message have been removed]
> > 
> >  
> > 
> > 
> > 
> > 
> > 
> > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
appropriate folder in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf 
and press the "search" button.
> >  
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@...
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/