Re: [EnergyPlus_Support] Fan pressure rise question
In this case, it would be nice to be able to simply enter motor efficiency and
total power input. I will post a suggestion for that. Looking in the
Engineering Reference (p. 537, pdf p. 571), the equation for fan power for HVAC
system fans (which is the same model used in the VENTILATION object) is:
Qtot[W]=mdot[kg/s]*deltaP[Pascals]/(TotalEfficiency*density[kg/m3])
or
Qtot[W]=VolumeFlow[m3/s]*deltaP[Pascals]/TotalEfficiency
(Note: Pascals=N/m2, so [N/m2]*[m3/s]=[N-m/s]=[J/s]=[W])
or
deltaP[Pascals] = Qtot[W]*TotalEfficiency/VolumeFlow[m3/s]
where TotalEfficiency is MotorEfficiency*FanEfficiency
MJW
On 30 Jan 2007 at 8:34, carlosochoam wrote:
> Dear all,
>
> In the air flow object Ventilation, one of the required data to
> determine electric energy consumption of the fan is the fan pressure
> rise.
>
> Is there a simple way to determine it? For example, for a fan that
> could serve a room?
>
> Thanks a lot,
>
> Carlos
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/