Re: [EnergyPlus_Support] Window AC or Unitary
Both the Window AC and the Unitary System objects use the DX cooling
coil object Coil:DX:CoolingBypassFactorEmpirical. This cooling coil
object is probably what you will need to use.... cooling only, single stage.
Probably easiest for you to use the Window AC example. In EnergyPlus,
the Window AC object is a piece of zone equipment that is relatively
easy to define (see example file WindACAuto.idf). For the Unitary
System object, you need to define an air loop which means additional
inputs that are probably not needed for what you are doing.
Don
ooikoonbeng2004 wrote:
>i have been asked to verify (and validate?) E+ simulation results by
>taking actual measurements with anemometer (for air flow rates),
>temperature sensors, maybe including RH sensors, if available, in a
>room air conditioned, cooling only, by a York or Carrier split
>(evaporator inside the room and air cooled condensor outside the room)
>air conditioner and a ELE weather station in a tropical climate.
>
>i plan to do this from 16th to 20th April this year. There is a Window
>AC example and a Unitary equipment class. Which one is more
>appropriate to this split type of airconditioner? Any advice from
>developers in this typer of work would be most welcomed. Many Thanks.
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/