[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Re: Ungodly number of errors
Yes, the low temperature could cause the controller message. Typically
this would be a HW
coil that is cooling or a ChW coil that is heating. It seems the problem
is in Plant.
Fred Buhl
brianstreby wrote:
> Just a quick follow-up to clarify-
>
> I'm pretty comfortable with the surface warnings in the error file. The
> errors that concern me include the following:
>
> ** Warning ** No valid range found for Loop Demand=726610.25 in Load
> Range Based Operation Scheme=BLR STAGING.
> ** Severe ** Controller error for controller = RTU-2 HW COIL VALVE
> ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC
> loops
> ** Warning ** Branch flow rates out of bounds in FlowResolver
>
> I checked into the controller error and found nothing wrong with the
> controller setup. From the Boiler Report, it appears that the hot water
> temperatures are extremely low (i.e. < 10 deg C), which I suspect could
> cause a controller issue. Also, I have two boilers in parallel and set
> a minimum hot water loop flow rate of 80 gpm (2.52 kg/s) and use a load-
> side bypass. From summer month data in the boiler report, it appears
> that the minimum loop flow was applied to each boiler, rather than the
> loop as a whole. In other words, I was expecting to see 40 gpm flow
> through each boiler in the summer but found that it was 80.
>
> Regards,
>
> Brian
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "brianstreby"
> <brianstreby@...> wrote:
>
>> My simulation is running and I get results, however, my error output
>> file has an obscene amount of severe errors and warnings (and results
>> in the output spreadsheet are a bit whacky too). I found diagnosing
>> errors that occurred during the compiling stage fairly easy, but the
>> ones that appear during the simulation seem more obscure. I am not
>> quite sure where to begin... Any advice?
>>
>> I've uploaded my input/output to the .../_Problem_ Submittals/ PSU_WB
>> directory in .zip format with today's date.
>>
>>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/