[EnergyPlus_Support] some strange things about the chiller control
Hi guys,
When using ¡®Plant Operation Schemes¡¯ to control the chillers, usually I choose Cooling Load Range Based Operation. But when I setLoadRange (Lower) Upper Limit according to the capacity of the chillers, the electricity consumption of chillers are very strange. Then I set the limits as 10 times of the capacity. Then the results seem very ¡®normal¡¯.
For example, if the capacity of one chiller is 2813,000 W, my code should be like the following way to make the running successful.
Why??
!- === ALL OBJECTS IN CLASS: COOLINGLOADRANGE BASED OPERATION ===
COOLINGLOADRANGE BASED OPERATION,
Chilled water loop Chiller Operation All Hours, !- Name
0, !-LoadRange Lower Limit 1 {W}
28130000, !-LoadRange Upper Limit 1 {W}
One Chiller, !- Priority Control Equip List Name 1
28130000, !-LoadRange Lower Limit 2 {W}
56260000, !-LoadRange Upper Limit 2 {W}
Two Chillers, !- Priority Control Equip List Name 2
56260000, !-LoadRange Lower Limit 3 {W}
9000000000, !-LoadRange Upper Limit 3 {W}
Chilled water loop All Chillers; !- Priority Control Equip List Name 3
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/