Re: [EnergyPlus_Support] Vertical Stack to induce natural ventilation
Ooi:
The Airflow Network model is not a good model to simulate natural
ventilation in a vertical stack. The main reason is that the model does not
have a component to deal with large horizontal openings accurately for the
time being.
However, you may try it with following suggestions using the AirflowNetwork
model:
1 Create one or more zones for a vertical stack
2 Create a zone you would like to ventilate
3 Use a component (AirflowNetwork:Multizone:Component Detailed Opening)
to connect the vetilated zone and the vertical stack zone.
4 If you create more vertical stack zones, use the same compoent to
connect two vertical stack zones. One way flow will be obtained from
horizontal openings.
5 Follow rules of the AirflowNetwork model to create a network. See
references to get detailed information.
Please let me know what happens.
Lixing Gu
----- Original Message -----
From: "ooikoonbeng2004" <kooi@xxxxxxxxxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, February 19, 2007 6:59 AM
Subject: [EnergyPlus_Support] Vertical Stack to induce natural ventilation
> Dear all,
>
> i was asked whether i can simulate the natural ventilation in a
> vertical stack that has been painted black, installed to induce such
> (natural ventilation) on a building in the tropics.
>
> i looked through (hopefully i have not missed anything) the
> documentation on Airflow Network but the openings of doors and windows
> are oriented ninety degrees from the above.
>
> Many thanks and with loving kindness,
> ooi
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press
> the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/