First, check REPORT, Surfaces, Details; and make sure that all 5 surfaces 
enclosing the attic have the correct azimuth and tilt (result go in the eio 
output file).  If these are correct, you might try breaking the two large 
sloped surfaces into two surfaces each.  In extreme geometry situations, the 
view factor algorithm sometimes works better with several small surfaces rather 
than a few large ones.

Mike


On 25 Feb 2007 at 23:46, Ian Doebber wrote:

> I receive the following error on a slightly strange geometry (an attic
> space in an A-Frame building so the ceiling has two sloped sides and one
> flat part).  Would this error be based just on the geometry or should I
> start digging into the coordinates.  What kind of results am I getting
> know with this error such as will it throw my energy balance off? 
> 
> 
> 
>    ** Severe  ** View factors not complete. Probably bad surface
> descriptions in zone="OPEN_LAB_404".
> 
>    **   ~~~   ** Enforced reciprocity has tolerance (ideal is
> 0.0)=1.3595E-002
> 
> 
> 
> Thanks
> 
> 
> 
> Ian Doebber
> 
> Arup
> 
> Mechanical Engineer
> 
> Office : 415-946-0292
> 
> Fax : 415-957-9096
> 
> Cell : 415-613-4314
> 
> 
> 
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup  business
> systems are scanned for acceptability of content and viruses
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Groups gets a make over. See the new email design.
http://us.click.yahoo.com/hOt0.A/lOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/