RE: [EnergyPlus_Support] What is the accurate component name?
Hi,
The reason for this type of error is that you have specified that one of the branch (LITTLE CHILLER BRANCH in this case) contains a particular component type (CHILLER:CONST COP in this case), and a component name (LITTLE CHILLER in this case). However when you are defining the CHILLER:CONST COP object the name you specified is not "LITTLE CHILLER". Check you dont have a typo in the CHILLER:CONST COP name field and make sure it matches with the name field in the branch definition.
Thanks
Sankar
S.K.Padhmanabhan
Research Associate
Mechanical & Aerospace Engineering
Oklahoma State University,
Stillwater, OK - 74075
Ph: (405)744-4380
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of love9787m
Sent: Fri 3/16/2007 2:51 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] What is the accurate component name?
Hi!
I'm currently simulating the DOAS.
As continuing the simulation, I refered to the example file in energy
plus and then filled out all the blanks that would be necessary.
But I found the message like this,
** Severe ** During Branch Input, Invalid Component Name
input=LITTLE CHILLER
** ~~~ ** Component type=CHILLER:CONST COP
** ~~~ ** Occurs on Branch=LITTLE CHILLER BRANCH
** Severe ** During Branch Input, Invalid Component Name
input=LITTLE CHILLER
** ~~~ ** Component type=CHILLER:CONST COP
** ~~~ ** Occurs on Branch=LITTLE CHILLER CONDENSER BRANCH
Especially, Component name is equal name at the example file.
What is the main reason for this? I couldn't find accurate component
name, Please let me the reason or component name
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Groups gets a make over. See the new email design.
http://us.click.yahoo.com/hOt0.A/lOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/