At 06:42 AM 3/18/2007, love9787m wrote:
>** Severe ** Single Heating Setpoint Schedule not found=HEATING SETPOINTS
>** ~~~ ** Reference SINGLE HEATING SETPOINT object=HEATING SETPOINT WITH SB

You've specified a Single Heating Setpoint object with name Heating 
Setpoint with SB that references a heating setpoint schedule named 
"Heating Setpoints" but there is no schedule named Heating Setpoints.

>** Severe ** Single Cooling Setpoint Schedule not found=COOLING SETPOINTS
>** ~~~ ** Reference SINGLE COOLING SETPOINT object=COOLING SETPOINT WITH SB

Same as above only Cooling.

>** Severe ** Schedule=ZONE CONTROL TYPE SCHED
>** ~~~ ** ..specifies control type 4 (Dual Set Point with Deadband) 
>as the control type. Not valid for this zone.
>** ~~~ ** ..reference ZONE CONTROL:THERMOSTATIC=ZONE 152 THERMOSTAT
>** ~~~ ** ..reference ZONE=152


In Zone=152, you've put in a Zone Control:Thermostatic called "Zone 
152 Thermostat"
that references a schedule called "Zone Control Type Sched".  That 
schedule specifies control type 4 -- Dual Set point with Deadband but 
your Thermostatic control does not allow for that type in this zone.




Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
See what's inside the new Yahoo! Groups email.
http://us.click.yahoo.com/0It09A/bOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/