Re: [EnergyPlus_Support] Zone controls and thermostats
Zone sensible load predicted gives you the thermostat load. If it is
zero, there is no load. The zone temperature is below the cooling set
point and/or above the heating set point. This is the thremostat dead
band region. The zone sensible load to heating setpoint predicted is
negative because the zone temperature is above the heating set point.
The zone sensible load to cooling setpoint predicted is positive because
the zone temperature is below the cooling set point.
Change your thermostat set points and you will see that when there is a
cooling load, the zone sensible load to cooling setpoint predicted will
go negative when the zone temperature is above the cooling setpoint. And
when there is a heating load, the zone sensible load to heating setpoint
will go positive when the zone temperature is below the heating
setpoint. The zone sensible load predicted should also show these same
results.
If your thermostat setpoints are correct, you will have to change the
zone loads. More outside air will likely cause a load in the zone for
both winter and summer. Or adding equipment/lighting loads will cause a
cooling load in summer (and possibly winter).
jeongch1004 wrote:
> Please help me!!
> I want to calculate "zone sensible load predicted", "zone sensible load
> to heating setpoint predicted", and "zone sensible load to cooling
> setpoint predicted" simply against setpoint.
> So, I entered value in "zone controls and thermostats" object
> But result value was different from "input/output referance" statement.
> concretely, "Zone sensible load predicted" results are all 0, "zone
> sensible load to heating setpoint predicted" results are all negative
> values, and "zone sensible load to cooling setpoint predicted" results
> are all positive values.
> I didn't enter that involved in system, except "Zone controls and
> thermostats" and "schedule" class.
> Why did it result like upper?
> Does It need that I enter additional value for other field...
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Something is new at Yahoo! Groups. Check out the enhanced email design.
http://us.click.yahoo.com/kOt0.A/gOaOAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/