Re: [EnergyPlus_Support] how to describe the air partition between perimeter zone and interior zone



My apologies for the slow response.

This is a difficult feature to model.  Material:Air will not transmit light, it 
is simply a resistive layer.

1.  A window subsurface is required to transmit solar and visible light from 
the perimeter zone to the interior zone.

2.  If the two zones will generally be controlled to the same temperature, then 
air exhange between the perimeter and interior can be neglected.  If a 
significant temperature difference is expected, then MIXING, CROSS MIXING, or 
AIRFLOWNETWORK:* objects are required to model the air exchange.

3.  There is currently no method for modeling radiant exchange between surfaces 
in different zones.

Mike







On 6 Mar 2007 at 15:58, nicole chen wrote:

> Dear all
> 
> How to set the construction of the vitual wall between perimeter zone and
> interior zone. Should Material:Air be applyed? If yes, the light and heat
> can go through this air wall partition? And how to set the thickness of this air
> wall ? Thank you in advance.
> 
> -- 
> Yours
> Nicole Chen
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/