The SYSTEM SIZING object is interacting with the ZONE SIZING. When a user-
specified supply air flow rate is present in the SYSTEM SIZING object, the
sizing algorithm assumes the users wants to scale all of the zone supply air
flow rates to match the specified value. This is altering the PTAC autosized
flow rates. The following change will fix this:
Exisiting SYSTEM SIZING object contains:
flow/system, !- cooling design air flow method
3.1152, !- cooling design air flow rate {m3/s}
flow/system, !- heating design air flow method
3.1152; !- heating design air flow rate {m3/s}
Change these lines to:
design day, !- cooling design air flow method
, !- cooling design air flow rate {m3/s}
design day, !- heating design air flow method
; !- heating design air flow rate {m3/s}
This will eliminate the interaction of the system sizing object and the zone
sizing. This requires that the DOAS be fully hard-sized (or nearly so). In
this input file, that is the case.
Mike
On 9 Mar 2007 at 22:04, asheaffe wrote:
> I have been trying to get a DOAS model working with PTACs. The model
> is posted as D1C_397. It uses a central system to deliver ventilation
> air at a constant 20C and PTACs to heat or cool from there to
> thermostat setpoints. The problem I am having is that the PTAC sizing
> is inaccurate and doesn't respond to changes in the zone sizing
> object. I had talked to Mike Witte before about this model and we
> agreed that this method should work. Any Ideas?
>
> Thanks,
>
> Andrew
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the
> "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.idf and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/