Re: [EnergyPlus_Support] Controller error in Air prime loop



It looks like you need 2 controllers for your input file. 1 for the 
primary air loop (Controller:Simple) and 1 for the outside air system 
(Controller:Outside Air). From your description, it sounds like you are 
trying to use the same controller in both places.

love9787m wrote:

> Hi.
> Now, I'm simulating on DOAS and VAV Singleduct System to check out
> the difference between those two systems.
> Due to fatal error from controller at Air prime loop field.
> The results are below
>
> ** Severe ** Invalid Controller Type=CONTROLLER:SIMPLE
> ** ~~~ ** ..reference Controller Name=OA SYS CONTROLLER 1
> ** ~~~ ** ..reference Controller List Name=OA SYS 1
> CONTROLLERS
> ** ~~~ ** ..reference Outside Air System=OA SYS 1
> ** ~~~ ** ....Controllers in OA Systems must be of
> type=CONTROLLER:OUTSIDE AIR
> ** Fatal ** Errors found in getting OUTSIDE AIR SYSTEM
> This is a first error message andthen modifing the controller type
> the result is below
>
> ** Fatal ** ManageControllers: Invalid controller=OA SYS
> CONTROLLER 1. The only valid controller type for an Air Primary Loop
> is CONTROLLER:SIMPLE.
> There are only two types of controllers. what is the problem of this
> case?
>
>  


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/