Re: [EnergyPlus_Support] A question about Supply Fan.
If you want to know how much fan energy is consumed in cooling mode and
how much fan energy is consumed in heating mode, then you will have to
use a spreadsheet to perform the calculations. Report the fan, cooling
and heating energy. Then in the spreadsheet, sum the fan energy when
cooling energy is greater than 0. Do the same for the fan when heating
energy is greater than 0.
Richard Raustad wrote:
> Use the Fan Electric Power and Fan Electric Consumption report
> variables. These variables are described in the InputOutputReference
> document for the Fan:Simple:OnOff object.
>
> xjtu.guowei wrote:
>
> > Dear All:
> >
> > I am doing a building simulation in which the compact HVAC is used.
> > There is a field which is supply fan operation mode. I have chosen the
> > cycling in stead of continuous. You know the fan will be working when
> > either cooling or heating needs to be supplied to the zone.
> >
> > I would like to know how much of the power consumed by the supply fan
> > is combining with the cooling or heating separately not totally.
> >
> > Thank you very much.
> >
> > wei
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
> [Non-text portions of this message have been removed]
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/