Dear Richard,
Thank you very much for your answer.
We followed your indications about the fan configuration and the exterior
node for the water heater but we didn?t notice any significant difference.
We are worry about some variable results of the heatpump components. We were
expecting to have similar annual results in the variables:
* Water Heater Source Rate (source coil of the water tank)
* DX Coil Total Water Heating Rate (hot water coil of the heat pump)
The mean difference between these variables is about 8% (much more than the
condenser pump power).
We also can?t understand the energy balance in the water heater tank. We
have simulated an almost ideal tank with a gas heater (Heater Thermal
Efficiency =1, with almost no heat loses), so we were expecting something
like:
* Water Heater Use Rate = Water Heater Source Rate + Water Heater Gas
Consumption Rate
But the power entering the water heater (Water Heater Source Rate + Water
Heater Gas Consumption Rate) is about 55% bigger than the ?Water Heater Use
Rate?
Can you help us with this question?
Thanks again for your attention.
Miguel Ángel Pascual
Director Técnico
MIYABI espacios urbanos bioclimáticos
Leyre 11bis, 1ºC 31002 Pamplona
Tel: 948 20 36 44 Fax: 948 20 78 60
Email: mapascual@xxxxxxxxx
Web: <http://www.miyabi.es/> www.miyabi.es
_____
De: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] En nombre de Richard Raustad
Enviado el: viernes, 30 de marzo de 2007 18:00
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
Asunto: [EnergyPlus_Support] Re: ProblemHeatPumpWaterHeater
You will also need to change the input for Ambient Temperature Indicator
in the Water Heater:Mixed object from Exterior to Outside Air Node.
Richard Raustad wrote:
> The heat pump water heater has an error when the HPWH is located
> outdoors and a draw through fan is used. Change your fan configuration
> to blow through. This problem will be corrected for the next release
> of EnergyPlus V2.0 in April 2007. You will also need to add a node
> name for the Ambient Temperature Outside Air Node in the Water
> Heater:Mixed object.
>
> Yahoo! Groups Notification wrote:
>
>> Hello,
>>
>> This email message is a notification to let you know that
>> a file has been uploaded to the Files area of your EnergyPlus_Support
>> group.
>>
>> File : /_Problem_Submittals/ProblemHeatPumpWaterHeater.idf
>> Uploaded by : jm22168 <jmartinez@miyabi. <mailto:jmartinez%40miyabi.es>
es> Description : Problems
>> with Heat Pump Water Heater
>> You can access the file at the URL:
>> http://groups.
<http://groups.yahoo.com/group/EnergyPlus_Support/files/_Problem_Submittals/
ProblemHeatPumpWaterHeater.idf>
yahoo.com/group/EnergyPlus_Support/files/_Problem_Submittals/ProblemHeatPump
WaterHeater.idf
>>
>> Your group is currently configured to send you email
>> notification whenever a member uploads a file. To turn off
>> notification, visit:
>> http://groups. <http://groups.yahoo.com/group/EnergyPlus_Support/join>
yahoo.com/group/EnergyPlus_Support/join
>>
>> Thank you for choosing Yahoo! Groups as your email group
>> service for the EnergyPlus_Support group.
>>
>> Regards,
>>
>> Yahoo! Groups Customer Care
>>
>> Your use of Yahoo! Groups is subject to
>> http://docs. <http://docs.yahoo.com/info/terms/> yahoo.com/info/terms/
>>
>>
>>
>>
>>
>>
>>
>>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec. <http://www.fsec.ucf.edu> ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/