[EnergyPlus_Support] Re: Residential heater sizing and cycling question
Mike thanks for the reply.
I'm not real familiar with the HVAC options, I normally use purchased air.
But I've look through the docs, and I'm looking for clarification.
What I'm hoping to be able to simulate is the effect of over-sizing
residential forced air heaters, and the effect of variable BTU/air volume
vs. Const. BTU/air volume, and their impact on heater efficiency (due to
heater cycling effect on combustion efficiency, burner/flue reheat, etc).
That is I'm hoping that, if I oversize, I should see more cycling, and less
efficiency. Is this feasible in E+?
As Don and Rich have explained, the HVAC system timestep does vary, and you
can
report results at the timestep level, but this is not relevant to what you
are
trying to model. Each HVAC timestep in EnergyPlus is a quasi-steady-state
simulation. For the gas heating coil cycling loss is modeled by looking at
the
quasi-steady part load ratio and making an adjustment to the efficiency
through
the "Part load fraction correlation (function of part load ratio)" curve in
COIL:Gas:Heating.
For example, if the load on the furnace from 9:00am to 9:30 am is 50% of
capacity, it doesn't matter if EnergyPlus simulates two 15-minute HVAC
timesteps, or 30 1-minute HVAC timesteps. Each timestep will evaluate the
efficiency at 50% part-load. There may be minor differences in results when
the timestep shifts down, but you should not need to be concerned with the
length of timestep. But, you do need to make sure the Part load fraction
correlation curve accurately represents the type of equipment you are
studying.
Mike
On 4 Apr 2007 at 10:30, taharvey2001 wrote:
> I'd like to be able to model a standard constant volume residential
> forced air heater in EnergyPlus and see the impact of Sizing on
> efficiency and heater cycling.
>
> I haven't been able to figure out how to model the heater
> appropriately in E+ or and make sure the heater has sufficiently small
> timestep resolution so the heater can cycle, and the difference in
> efficiency can be seen.
>
> As I understand, the HVAC system timestep is decoupled from the 15
> minute building timestep, allowing it to free-run with an adaptive
> timestep (down to seconds if need be) - is this true, and is there
> anything that need to be done to enable this behavior? Is there anyway
> to see the high-res HVAC transients in the output?
>
> What is the best way to get a const. volume, const BTU heater to model
> residential forced air systems?
>
> thanks,
>
> troy
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/