[EnergyPlus_Support] purchased air problem....
Hi I am new to energy plus and I have a proble with purchased air. I am following the example from file purchairtables.idf and i get the following errors...
Any ideas ?
This is the erros
** Severe ** Node Connection Error, Node="NODE_1", ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=HOME1
** Severe ** Node Connection Error, Node="NODE_2", ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=HOME2
** Severe ** Node Connection Error, Node="NODE_3", ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=HOME3
** Severe ** Node Connection Error, Node="NODE_4", ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=HOME4
** Severe ** Node Connection Error, Node="NODE_5", ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=HOME5
** Severe ** Node Connection Error, Node="NODE_6", ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=HOME6
** Severe ** Node Connection Error, Node="NODE_7", ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP CONFIGURATION, Name=KLIMAKOSTASIO
************* There were 7 node connection errors noted.
This is the part from my input file
!- =========== ALL OBJECTS IN CLASS: NODE LIST ===========
NODE LIST,
Home 1 Inlets, !- Node List Name
NODE_1; !- Node_ID_1
NODE LIST,
Home 2 Inlets, !- Node List Name
NODE_2; !- Node_ID_1
NODE LIST,
Home 3 Inlets, !- Node List Name
NODE_3; !- Node_ID_1
NODE LIST,
Home 4 Inlets, !- Node List Name
NODE_4; !- Node_ID_1
NODE LIST,
Home 5 Inlets, !- Node List Name
NODE_5; !- Node_ID_1
NODE LIST,
Home 6 Inlets, !- Node List Name
NODE_6; !- Node_ID_1
NODE LIST,
Klimak Inlets, !- Node List Name
NODE_7; !- Node_ID_1
!- =========== ALL OBJECTS IN CLASS: CONTROLLED ZONE EQUIP CONFIGURATION ===========
CONTROLLED ZONE EQUIP CONFIGURATION,
Home1, !- Zone Name
Home 1 Equipment, !- List Name: Zone Equipment
Home 1 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s)
, !- Node List or Node Name: Zone Air Exhaust Node(s)
NODE_8, !- Zone Air Node Name
NODE_9; !- Zone Return Air Node Name
CONTROLLED ZONE EQUIP CONFIGURATION,
Home2, !- Zone Name
Home 2 Equipment, !- List Name: Zone Equipment
Home 2 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s)
, !- Node List or Node Name: Zone Air Exhaust Node(s)
NODE_10, !- Zone Air Node Name
NODE_11; !- Zone Return Air Node Name
CONTROLLED ZONE EQUIP CONFIGURATION,
Home3, !- Zone Name
Home 3 Equipment, !- List Name: Zone Equipment
Home 3 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s)
, !- Node List or Node Name: Zone Air Exhaust Node(s)
NODE_12, !- Zone Air Node Name
NODE_13; !- Zone Return Air Node Name
CONTROLLED ZONE EQUIP CONFIGURATION,
Home4, !- Zone Name
Home 4 Equipment, !- List Name: Zone Equipment
Home 4 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s)
, !- Node List or Node Name: Zone Air Exhaust Node(s)
NODE_14, !- Zone Air Node Name
NODE_15; !- Zone Return Air Node Name
CONTROLLED ZONE EQUIP CONFIGURATION,
Home5, !- Zone Name
Home 5 Equipment, !- List Name: Zone Equipment
Home 5 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s)
, !- Node List or Node Name: Zone Air Exhaust Node(s)
NODE_16, !- Zone Air Node Name
NODE_17; !- Zone Return Air Node Name
CONTROLLED ZONE EQUIP CONFIGURATION,
Home6, !- Zone Name
Home 6 Equipment, !- List Name: Zone Equipment
Home 6 Inlets, !- Node List or Node Name: Zone Air Inlet Node(s)
, !- Node List or Node Name: Zone Air Exhaust Node(s)
NODE_18, !- Zone Air Node Name
NODE_19; !- Zone Return Air Node Name
CONTROLLED ZONE EQUIP CONFIGURATION,
Klimakostasio, !- Zone Name
Klimak Equipment, !- List Name: Zone Equipment
Klimak Inlets, !- Node List or Node Name: Zone Air Inlet Node(s)
, !- Node List or Node Name: Zone Air Exhaust Node(s)
NODE_20, !- Zone Air Node Name
NODE_21; !- Zone Return Air Node Name
!- =========== ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST ===========
ZONE EQUIPMENT LIST,
Home 1 Equipment, !- Name
PURCHASED AIR, !- KEY--Zone Equipment Type 1
Home 1 Purchased air, !- Type Name 1
1, !- Cooling Priority 1
1; !- Heating Priority 1
ZONE EQUIPMENT LIST,
Home 2 Equipment, !- Name
PURCHASED AIR, !- KEY--Zone Equipment Type 1
Home 2 Purchased air, !- Type Name 1
1, !- Cooling Priority 1
1; !- Heating Priority 1
ZONE EQUIPMENT LIST,
Home 3 Equipment, !- Name
PURCHASED AIR, !- KEY--Zone Equipment Type 1
Home 3 Purchased air, !- Type Name 1
1, !- Cooling Priority 1
1; !- Heating Priority 1
ZONE EQUIPMENT LIST,
Home 4 Equipment, !- Name
PURCHASED AIR, !- KEY--Zone Equipment Type 1
Home 4 Purchased air, !- Type Name 1
1, !- Cooling Priority 1
1; !- Heating Priority 1
ZONE EQUIPMENT LIST,
Home 5 Equipment, !- Name
PURCHASED AIR, !- KEY--Zone Equipment Type 1
Home 5 Purchased air, !- Type Name 1
1, !- Cooling Priority 1
1; !- Heating Priority 1
ZONE EQUIPMENT LIST,
Home 6 Equipment list, !- Name
PURCHASED AIR, !- KEY--Zone Equipment Type 1
Home 6 Purchased air, !- Type Name 1
1, !- Cooling Priority 1
1; !- Heating Priority 1
ZONE EQUIPMENT LIST,
Klimak Equipment , !- Name
PURCHASED AIR, !- KEY--Zone Equipment Type 1
Klimak Purchased air, !- Type Name 1
1, !- Cooling Priority 1
1; !- Heating Priority 1
!- =========== ALL OBJECTS IN CLASS: PURCHASED AIR ===========
PURCHASED AIR,
Home 1 Purchased air, !- Purchased Air Name
NODE_1, !- Zone Supply Air Node Name
50, !- Heating Supply Air Temp {C}
13, !- Cooling Supply Air Temp {C}
0.02, !- Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.02, !- Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
NO LIMIT, !- heating limit
autosize, !- Maximum heating air flow rate {m3/s}
NO LIMIT, !- cooling limit
autosize, !- Maximum cooling air flow rate {m3/s}
NO OUTSIDE AIR, !- outside air
autosize; !- Outside air flow rate {m3/s}
PURCHASED AIR,
Home 2 Purchased air, !- Purchased Air Name
NODE_2, !- Zone Supply Air Node Name
50, !- Heating Supply Air Temp {C}
13, !- Cooling Supply Air Temp {C}
0.02, !- Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.02, !- Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
NO LIMIT, !- heating limit
autosize, !- Maximum heating air flow rate {m3/s}
NO LIMIT, !- cooling limit
autosize, !- Maximum cooling air flow rate {m3/s}
NO OUTSIDE AIR, !- outside air
autosize; !- Outside air flow rate {m3/s}
PURCHASED AIR,
Home 3 Purchased air, !- Purchased Air Name
NODE_3, !- Zone Supply Air Node Name
50, !- Heating Supply Air Temp {C}
13, !- Cooling Supply Air Temp {C}
0.02, !- Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.02, !- Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
NO LIMIT, !- heating limit
autosize, !- Maximum heating air flow rate {m3/s}
NO LIMIT, !- cooling limit
autosize, !- Maximum cooling air flow rate {m3/s}
NO OUTSIDE AIR, !- outside air
autosize; !- Outside air flow rate {m3/s}
PURCHASED AIR,
Home 4 Purchased air, !- Purchased Air Name
NODE_4, !- Zone Supply Air Node Name
50, !- Heating Supply Air Temp {C}
13, !- Cooling Supply Air Temp {C}
0.02, !- Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.02, !- Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
NO LIMIT, !- heating limit
autosize, !- Maximum heating air flow rate {m3/s}
NO LIMIT, !- cooling limit
autosize, !- Maximum cooling air flow rate {m3/s}
NO OUTSIDE AIR, !- outside air
autosize; !- Outside air flow rate {m3/s}
PURCHASED AIR,
Home 5 Purchased air, !- Purchased Air Name
NODE_5, !- Zone Supply Air Node Name
50, !- Heating Supply Air Temp {C}
13, !- Cooling Supply Air Temp {C}
0.02, !- Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.02, !- Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
NO LIMIT, !- heating limit
autosize, !- Maximum heating air flow rate {m3/s}
NO LIMIT, !- cooling limit
autosize, !- Maximum cooling air flow rate {m3/s}
NO OUTSIDE AIR, !- outside air
autosize; !- Outside air flow rate {m3/s}
PURCHASED AIR,
Home 6 Purchased air, !- Purchased Air Name
NODE_6, !- Zone Supply Air Node Name
50, !- Heating Supply Air Temp {C}
13, !- Cooling Supply Air Temp {C}
0.02, !- Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.02, !- Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
NO LIMIT, !- heating limit
autosize, !- Maximum heating air flow rate {m3/s}
NO LIMIT, !- cooling limit
autosize, !- Maximum cooling air flow rate {m3/s}
NO OUTSIDE AIR, !- outside air
autosize; !- Outside air flow rate {m3/s}
PURCHASED AIR,
Klimak Purchased air, !- Purchased Air Name
NODE_7, !- Zone Supply Air Node Name
50, !- Heating Supply Air Temp {C}
13, !- Cooling Supply Air Temp {C}
0.02, !- Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.02, !- Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
NO LIMIT, !- heating limit
autosize, !- Maximum heating air flow rate {m3/s}
NO LIMIT, !- cooling limit
autosize, !- Maximum cooling air flow rate {m3/s}
NO OUTSIDE AIR, !- outside air
autosize; !- Outside air flow rate {m3/s}
Thank you
Odoumpozanis Kostas
Kozani, Greece
24/04/2007
---------------------------------
Ahhh...imagining that irresistible "new car" smell?
Check outnew cars at Yahoo! Autos.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/