Re: [EnergyPlus_Support] ground heat transfer modeling for unconditioned spaces
Presently, the recommended approach would be #1, an iterative approach. I
think that you will find it to converge rather quickly.
If you have many cases like this, you may want to compare option 2 with option
1 for a couple of climates (warmer and colder) and see how much difference
there is.
I will add a more integrated approach for such applications to the overall
enhancement wish list.
Mike
On 25 Apr 2007 at 10:17, Spencer, Justin wrote:
> I'm looking for a good way to model ground heat transfer from
> unconditioned spaces. The basement and slab programs require an input
> temperature for the space. This isn't too hard to provide when you have
> a conditioned space - you should be able to get close. Since the ground
> transfer is driven by a small temperature difference between the space
> and the ground temperature, getting this temperature wrong will have a
> big impact on the resulting ground temperatures and energy balance in
> the space.
>
>
>
> In particular, a ventilated crawlspace with some amount of duct leakage
> into the space creates a real modeling conundrum, since the ground
> transfer is one small part of the temperature in the space. I can think
> of 2 possible solutions:
>
> 1. Use an iterative approach. Run the basement model with a guess
> at the temperatures in the space, then run the resulting ground
> temperatures in the full simulation, make a new guess at the
> temperatures in the space, run the basement model, until convergence is
> reached. (iterative approach)
> 2. Abandon the basement model. Ignore ground transfer through the
> floor. Model the walls with regular 1-D walls, with wall properties
> that approximate the soil and wall performance. (Perimeter conduction
> approach)
>
> In the long run, if the basement model ran with the actual building,
> instead of needing space temperatures as an input, then the basement
> model could be run once, instead of requiring exhaustive iteration.
>
>
>
> What's the best workaround to use in the short term?
>
>
>
> Justin Spencer
>
>
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/