Look in the InputOutputReference.pdf document... search for
"UnitarySystem:HeatPump:AirToAir".
For this system, you need to define an associated direct expansion (DX)
cooling coil [Coil:DX:CoolingBypassFactorEmpirical or
Coil:DX:CoolingHeatExchanger Assisted] and a DX heating coil
[Coil:DX:HeatingEmpirical]. The performance of the cooling and heating
coils is defined in these coil objects.
pezpapagallo wrote:
>Good afternoon, I´m simulating a room with a unitary heat pump...in my
>simulation I´m trying to define the cooling and heating powers but I
>don´t know were to define them...for example:
>
>cooling power=3500W
>Heating power=3700W
>Absorbed power during the maximum performance=1090W
>
>Thank you in advance
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/