[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Warmest Function Increases Boiler Natural Gas Usage?



Noel,

Please upload your input. Most likely you have conflicting
setpoint managers.

Fred

noelcrrl wrote:
> Mike-
>
> To answer your question...yes I do have a central heating coil.  I 
> paid special attention to the setpoint managers as you suggested.  I 
> have three set point managers, as follows:  
>
> 1)I have a mixed air set point manager that controls the mixed air 
> outlet and the cooling coil outlet.  
>
> 2)I have set point manager at the heating coil setting it 55F.
>
> 3)I have the warmest setpoint manager controlling the supply fan 
> outlet between 55F and 65F.  
>
> It seems that the heating coil continues to ignore the 55F setpoint 
> and heats the air to a higher temperature.
>
> Please advise?  Thanks in advance for your help.  
>
> Noel
>
>
>
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> <mjwitte@...> wrote:
>   
>> Rich addressed the fan power, chiller, and tower energy use.
>>
>> The increase in gas use is not right.  Is there a central heating 
>>     
> coil in this 
>   
>> VAV system?  Is it picking up it's setopint from the air loop 
>>     
> outlet node?  If 
>   
>> so, it may be warming cool mixed air to that some VAV damper 
>>     
> somewhere can stay 
>   
>> fully open at low cooling loads.  
>>
>> Be sure the heating coil setpoint is not linked in any way to what 
>>     
> the warmest 
>   
>> set point manager is doing for cooling.  No two setpoint managers 
>>     
> should be 
>   
>> setting a temperature setpoint on the same node.
>>
>> Mike
>>
>>
>> On 22 May 2007 at 0:22, noelcrrl wrote:
>>
>>     
>>> All-
>>>
>>> I am modeling the warmest function in a Hospital building.  The 
>>>       
> model 
>   
>>> is equipped with a VAV system (pre-heat coil, cooling coil, a 
>>>       
> central 
>   
>>> heating coil, & reheat coils).  I have the warmest setpoint node 
>>>       
> set 
>   
>>> at the supply fan outlet.  The warmest function is set up to 
>>>       
> deliver 
>   
>>> supply air between 55F and 60F.  Also, the chilled water is 
>>>       
> delivered 
>   
>>> to the cooling coils between 44F and 52F, depending on outside 
>>>       
> air 
>   
>>> temperature.  
>>>
>>> When I increase the upper limit of the warmest function from 60F 
>>>       
> to 
>   
>>> 65F and the chilled water upper limit from 52F to 54F, the 
>>>       
> natural 
>   
>>> gas consumption of the boiler increases by 7%.  In addition, the 
>>> supply fan energy usage increases by 6%.  The energy saving 
>>>       
> benefit 
>   
>>> of the chiller and the cooling tower, 2% and 3%, respectively, is 
>>>       
> not 
>   
>>> enough to overcome the boiler and fan energy usage increases.  
>>>       
> The 
>   
>>> overall energy usage (total facility) increases by 2%.
>>>
>>> I am confused to why this is happening?  How can increasing the 
>>>       
> reset 
>   
>>> temperatures increase overall energy consumption instead of 
>>> decreasing it?  Why is the heating energy usage increasing in 
>>>       
> this 
>   
>>> manner?
>>>
>>> Thanks in advance for your help.
>>>
>>> Noel
>>>
>>>
>>>
>>>
>>> The primary EnergyPlus web site is found at:
>>> http://www.energyplus.gov
>>>
>>> The group web site is:
>>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>>
>>> Attachments are not allowed -- please post any files to the 
>>>       
> appropriate folder
>   
>>> in the Files area of the Support Web Site.
>>>
>>> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
>>>       
> under the
>   
>>> Documentation link and press the "search" button.
>>>
>>> Yahoo! Groups Links
>>>
>>>
>>>
>>>
>>>
>>>       
>> ========================================================
>> Michael J. Witte, GARD Analytics, Inc.
>> EnergyPlus Testing and Support      
>> EnergyPlus-Support@...
>>
>>     
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>  
> Yahoo! Groups Links
>
>
>
>   


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/