The error message is incorrect.  It should read "Sensor node did not find a 
matching node of appropriate type (node type *other than* Actuator, Sensor, 
OutsideAir)."  But there is an error in the node names.  Whenever there are 
node connection errors, the first step to solving the problem is to search the 
input file for the node name listed in the error message.  Start with the 
CONTROLLED ZONE EQUIPMENT CONFIGURATION object for this zone.  There should be 
a node list for zone inlet node with 2 nodes listed, one which is the outlet 
from the unit ventilator and one which is the outlet from the DOAS terminal 
unit.  Make sure the node names match.  The SET POINT MANAGER:SINGLE ZONE 
COOLING object must also reference the zone inlet node name that matches the 
DOAS terminl unit.   Each problem you fix should get rid of two or more node 
conneciton errors.

Mike


On 31 May 2007 at 11:57, love9787m wrote:

> Now, Simulation DOAS coupled with unit ventilator.
> To figure out the optimal model, refer to example,idf files.
> (Unitvent 5Zone)
> Would please this node connection error below:
> 
> ** Severe  ** Node Connection Error, Node="ZONE 59 INLET NODE", 
> Sensor node did not find a matching node of appropriate type 
> (Actuator, Sensor, OutsideAir).
>    **   ~~~   ** Reference Object=SET POINT MANAGER:SINGLE ZONE 
> COOLING, Name=ZONE 59 COOLING MANAGER
>    ** Severe  ** Node Connection Error, Node="CW SUPPLY OUTLET 
> NODE", Setpoint node did not find a matching node of appropriate 
> type (Setpoint, OutsideAir).
>    **   ~~~   ** Reference Object=SET POINT MANAGER:SCHEDULED, 
> Name=CHILLED WATER LOOP SETPOINT MANAGER
>    ** Severe  ** Node Connection Error, Node="ZONE 59 UNITVENT 
> OUTLET NODE", ZoneInlet node did not find an outlet node.
>    **   ~~~   ** Reference Object=CONTROLLED ZONE EQUIP 
> CONFIGURATION, Name=59
>    ** Severe  ** Node Connection Error, Node="ZONE59EXHAUSTS", 
> ZoneExhaust node did not find a matching inlet node.
>    **   ~~~   ** Reference Object=CONTROLLED ZONE EQUIP 
> CONFIGURATION, Name=59
>    ** Severe  ** Node Connection Error, 
> Node="ZONE59UNITVENTAIRINLETNODE", Inlet node did not find an 
> appropriate matching "outlet" node.
>    **   ~~~   ** If this is an outside air inlet node, it must be 
> listed in an OUTSIDE AIR NODE or OUTSIDE AIR INLET NODE LIST object.
>    **   ~~~   ** Reference Object=UNIT VENTILATOR, 
> Name=ZONE59UNITVENT
>    ** Severe  ** Node Connection Error, 
> Node="ZONE59UNITVENTAIRINLETNODE", Inlet node did not find an 
> appropriate matching "outlet" node.
>    **   ~~~   ** If this is an outside air inlet node, it must be 
> listed in an OUTSIDE AIR NODE or OUTSIDE AIR INLET NODE LIST object.
>    **   ~~~   ** Reference Object=UNIT VENTILATOR-OA MIXER, 
> Name=ZONE59UNITVENT
>    ** Severe  ** Node Connection Error, 
> Node="ZONE59UNITVENTFANOUTLETNODE", Inlet node did not find an 
> appropriate matching "outlet" node.
>    **   ~~~   ** If this is an outside air inlet node, it must be 
> listed in an OUTSIDE AIR NODE or OUTSIDE AIR INLET NODE LIST object.
>    **   ~~~   ** Reference Object=COIL:WATER:COOLING, 
> Name=ZONE59UNITVENTCOOLINGCOIL
>    ** Severe  ** Node Connection Error, Node="ZONE 59 
> UNITVENTOAMIXER OUTLET NODE", Inlet node did not find an appropriate 
> matching "outlet" node.
>    **   ~~~   ** If this is an outside air inlet node, it must be 
> listed in an OUTSIDE AIR NODE or OUTSIDE AIR INLET NODE LIST object.
>    **   ~~~   ** Reference Object=FAN:SIMPLE:CONSTVOLUME, Name=ZONE 
> 59 UNITVENT FAN
> 
> I've tried to find the method that figures out those problems,
> I couldnot handle.
> Please help me
> 
> Regards
> Dae Woong Ha
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/