Re: [EnergyPlus_Support] Confusion over Fan in AirFlow Network
Ooi:
It seems the input file does not specify a fan as Zone2WindACFan, so that
the first error message occurs (GetFanIndex: Fan not found=Zone2WindACFan).
In other words, Zone2WindACFan is not listed in fan index. You may define
the fan in the AIRFLOWNETWORK:DISTRIBUTION:COMPONENT CONSTANT VOLUME FAN
object. Since the fan is not listed in the fan index, the prgram can not go
any further.
My suggestion is to disable the AirflowNetwork model first to see whether
you can eliminate the first error or not. The model disablement is to use
the choice of NO MULTIZONE OR DISTRIBUTION in the AirflowNetwork Control
field in the AirflowNetwork Simulation object. If you still have problems,
please upload the file. I will take a look.
By the way, Window AC is not supported for the time being if you use the
choice as MULTIZONE WITH DISTRIBUTION or MULTIZONE WITH DISTRIBUTION ONLY
DURING FAN OPERATION in the AirflowNetwork Control field in the
AirflowNetwork Simulation object
Thanks.
Lixing Gu
----- Original Message -----
From: "ooikoonbeng2004" <ooi_kb3@xxxxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, July 02, 2007 2:06 AM
Subject: [EnergyPlus_Support] Confusion over Fan in AirFlow Network
> Confusion over Fan
>
>
> Hello everyone,
>
> i am starting to use the AirFlow Network with only the
> MultiZone:Surfaces referring to the SIMPLE house example.
>
> From the .err file, a zone needs two surfaces and i have added a
> door to each zone. So, correct me if i am wrong, the air in the
> AirFlow Network goes through ceiling crack/leakage and door leakage.
>
> As i am only studying the thermal aspects of the building envelop, i
> do not use a Direct air or fan as in the Simple House example. But i
> have a Window AirConditioner in the second zone.
>
> The messages in .err file, includes:
>
> GetFanIndex: Fan not found=Zone2WindACFan
> GetAirflowNetworkINput: The fan type defined in
> AIRFLOWNETWORK:DISTRIBUTION:COMPONENT CONSTANT VOLUME FAN =
> ZONE2WINDACFAN is not allowed etc.
>
> The 'Fan' in the error message can only refer to the fan in Window
> AC. But how do i enter the index of this fan or overcome the errors
> in the .err file?
>
> kind regards,
> ooi
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/