We have an input file which uses the COIL:DX:CoolingBypassFactorEmpirical object and is causing some problems.

I have uploaded the example file HevacompDXCoolingProblem.zip.

When run through v1.4 an error is reported as follows:

   ** Severe  ** COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "WC:C2 FF OPEN" -- coil bypass factor calculation did not converge after max iterations.
   **   ~~~   ** The RatedSHR of 0.571, entered by the user or autosized (see *.eio file),
   **   ~~~   ** may be causing this. The line defined by the coil rated inlet air conditions
   **   ~~~   ** (26.7C drybulb and 19.4C wetbulb) and the RatedSHR (i.e., slope of the line) must intersect
   **   ~~~   ** the saturation curve of the psychrometric chart. If the RatedSHR is too low, then this
   **   ~~~   ** intersection may not occur and the coil bypass factor calculation will not converge.
   **   ~~~   ** If autosizing the SHR, recheck the design supply air humidity ratio and design supply air
   **   ~~~   ** temperature values in the System Sizing and Zone Sizing objects. In general, the temperatures
   **   ~~~   ** and humidity ratios specified in these two objects should be the same for each system
   **   ~~~   ** and the zones that it serves.

Given the absense of a system sizing object, I am unsure how else to address this problem. Any help would be appreciated.
Brian Aldred
Software Development
Tel: 0114 255 6680
Fax: 0114 255 6638



Hevacomp Ltd is a company registered in England and Wales with company number 1523216
Registered office: Smithywood House, Smithywood Crescent, Sheffield, S8 0NU 

P Help save paper - do you need to print this email?


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/