I think you can have only one simple Ventilation object per zone.  Multiple ventilation objects are on the wish list.  
 
Zone equipment (like Unit Ventilator) can serve as a second source of ventilation.
 
A full air loop system can serve as a third source of ventilation.  
 
The simple Infiltration object can be considered the same as ventilation.  
 
If you really need to, it is possible to do a modeling trick where an additional Ventilation object is used on a small dummy zone.  The dummy zone is connected to the main zone using a pair of Mixing objects. 
 
 

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx on behalf of w_jiang78
Sent: Mon 7/23/2007 2:05 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] ventilation



is it true that maximum of two ventilation objects serving one thermal 
zone is allowed? 
I have to use 3 ventilation systems serving the same zone because each 
of them has different control. 
It runs ok if I delete one though. 

Thanks.

Ashley



 


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/