[EnergyPlus_Support] Re: Cntroller input data problem.
Hi Everyone,
I also have the same problem.
** Severe ** FindRootSimpleController: Controller error for
controller = VAV SYS 2 COOLING COIL CONTROLLER
** ~~~ ** Occurrence info=CALGARY INT'L AB CAN WYEC2-B-25110
WMO#=718770, 01/31 09:00 - 10:00
** ~~~ ** Controller function is inconsistent with user
specified controller action = Reverse action
** ~~~ ** Actuator will be set to maximum action
** ~~~ ** Controller control type=Temperature
** ~~~ ** Controller temperature set point = 17.20 [C]
** ~~~ ** Controller sensed temperature = 17.37 [C]
** ~~~ ** Controller actuator mass flow rate set to 5.71 [kg/s]
** ~~~ ** Controller actuator temperature = 7.00 [C]
** ~~~ ** Note: Chilled water coils should be reverse action
and the entering chilled
** ~~~ ** water temperature (controller actuator
temperature) should be below the setpoint temperature
** ~~~ ** Note: Hot water coils should be normal action and
the entering hot
** ~~~ ** water temperature (controller actuator
temperature) should be above the setpoint temperature
I am also sure that the parameters for VAV SYS 2 COOLING COIL
CONTROLLER are right, because most of time the program can run
properly. It seem many factors can affect this error message. For
example, if I add more internal heat in rooms, then this error
message will not appear. I found this just because I input the wrong
values for internal heat.
Tj Ywh
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "love9787m" <love9787m@...>
wrote:
>
> ** Severe ** FindRootSimpleController: Controller error for
> controller = MAIN COOLING COIL CONTROLLER
> In the error message, Controller sensed temperature is 22288.16 [C].
> I've never seen before like this problem and sensed temperature
> never reached this high temperature.
> To find out the method, which part or object should I sheckand
> what is the reason for this problem?
>
> ** ~~~ ** Occurrence info=ULSAN - KOR IWEC DATA WMO#=471520,
> 07/03 05:40 - 05:41
> ** ~~~ ** Controller function is inconsistent with user
> specified controller action = Reverse action
> ** ~~~ ** Actuator will be set to maximum action
> ** ~~~ ** Controller control type=Temperature
> ** ~~~ ** Controller temperature set point = 15.00 [C]
> ** ~~~ ** Controller sensed temperature = 22288.16 [C]
> ** ~~~ ** Controller actuator mass flow rate set to 1.10
> [kg/s]
> ** ~~~ ** Controller actuator temperature = -120.36 [C]
> ** ~~~ ** Note: Chilled water coils should be reverse
> action and the entering chilled
> ** ~~~ ** water temperature (controller actuator
> temperature) should be below the setpoint temperature
> ** ~~~ ** Note: Hot water coils should be normal action and
> the entering hot
> ** ~~~ ** water temperature (controller actuator
> temperature) should be above the setpoint temperature
> ** Warning ** Calculated Humidity Ratio Invalid (PsyWFnTdbTwbPb)
>
> Please let me know the reason and method.
> Thank you in advance.
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/