Re: [EnergyPlus_Support] Daylighting Map: Strange dates & other related
The raw data output from your run does not appear to have a year
associated with the dates. E.g., here is what came out when I ran
your input file with the weather data:
Date/Time,CAIRO INTL AIRPORT AL QAHIRAH EGY ETMY
WMO#=623660:N:Illuminance [lux] (Hourly),RefPt1=(0.00:15.00:9.80),,,
01/01 07:00,x=-9.00,x=-6.00,x=-3.00,x=0.00,x=3.00,x=6.00,x=9.00
y=11.50,1,1,1,1,1,1,1
y=13.25,1,1,1,1,1,1,1
y=15.00,1,1,1,1,1,1,1
y=16.75,2,3,3,2,3,3,2
y=18.50,6,9,15,4,15,9,6
and so forth.
I notice in your files that things begin to come unglued at 1/12-1/13:
01/12/2007 16:00,x=-9.00,x=-6.00,x=-3.00,x=0.00,x=3.00,x=6.00,x=9.00
y=11.50,29,32,34,34,34,33,31
y=13.25,33,39,42,43,43,42,37
y=15.00,44,58,63,63,64,61,51
y=16.75,74,114,122,108,128,111,95
y=18.50,167,366,459,172,515,281,257
Date/Time,CAIRO INTL AIRPORT AL QAHIRAH EGY CUSTOM-623660
WMO#=623660:N:Illuminance [lux] (Hourly),RefPt1=(0.00:15.00:9.80),,,,,
01/01/2013 08:00,x=-9.00,x=-6.00,x=-3.00,x=0.00,x=3.00,x=6.00,x=9.00
y=11.50,15,16,16,16,16,15,14
y=13.25,18,19,20,20,19,18,15
y=15.00,24,27,29,28,28,26,20
y=16.75,46,50,59,50,56,54,33
y=18.50,134,134,259,86,224,188,80
So, I'm thinking that our "month/day" convention is causing you some
problems with your regional date convention or opening in Excel or
something similar. (After you open the file in a spreadsheet, it
has automatically read some things as dates and performed its own conversion).
EnergyPlus does read the regional date settings for some outputs
(e.g. the regular eso and meter files as I remember) but looks like
this may need to be applied for the Map output as well.
I will research a little more and write up a Change Request if that
appears to be the problem.
Sorry for the inconvenience. A work around for you might be to try
setting the regional date settings to month/day convention rather
than what you are now but I'm not sure that will work.
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/