[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Hot water radiators question
Yes, maybe. If the pump is variable speed, then yes. If the pump is constant
speeed, then you need a splitter, a bypass pipe, and a mixer on the demand
side.
By "radiator thermostat", you mean a SET POINT MANAGER:* object to control the
hot water supply temperature?
Yes, the example file is using purchased hot water (district heating) instead
of a boiler. You can substitute a BOILER:SIMPLE where you see PURCHASE:HOT
WATER referenced.
Mike
On 7 Aug 2007 at 16:22, katerina fragaki wrote:
> Dear Mike,
>
> Thanks for your reply. Is therefore a pump, a boiler, a radiator, a radiator
> thermostat and a room thermostat enough for the simplest possible modelling
> of a hot water radiator system?
>
> Also I noticed in the file that you suggest me to have as an example that it
> uses Purchased:Hot Water. Is this instead of using a boiler?
>
> Thanks,
> Katerina
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> What you have so far is fine, but it is not enough. There must be a
> complete
> PLANT LOOP and more components including a pump and boiler in order to serve the
> radiator. Please see example file WindACAuto.idf This example has three
> radiators on the demand side of the plant loop, but you can construct your input
> to be similar with a single radiator.
>
> Mike
>
> On 2 Aug 2007 at 9:59, katerina fragaki wrote:
>
> > Hello,
> >
> > I try to connect hot water radiators using Energy Plus and I am getting some
> > error messages so I wonder whether someone can help me with this. I try the
> > connections as follows (having already fiil in the fields of CONTROLLED ZONE
> > EQUIPEMENT CONFIGUGATION and ZONE EQUIPMENT LIST):
> >
> > BASEBOARD HEATER:Water:Convective
> > Baseboard Name HouseBaseboard
> > Available Schedule House_Zone_OPERATION
> > Inlet_Node HouseReheatWaterInletNode
> > Outlet_Node HouseReheatWaterOutletNode
> > UA 500
> > Max Water Flow Rate 0.0013
> > Convergence Tolerance 0.001
> >
> > And I am getting the following error messages:
> > ** Severe ** Node Connection Error, Node="HOUSEREHEATWATERINLETNODE", Inlet
> > node did not find an appropriate matching "outlet" node. ** ~~~ ** If this is
> > an outside air inlet node, it must be listed in an OUTSIDE AIR NODE or OUTSIDE
> > AIR INLET NODE LIST object. ** ~~~ ** Reference Object=BASEBOARD
> > HEATER:WATER:CONVECTIVE, Name=HOUSEBASEBOARD ** Warning ** Node Connection
> > Error for object BASEBOARD HEATER:WATER:CONVECTIVE, name=HOUSEBASEBOARD ** ~~~
> > ** Hot Water Nodes not on any Branch or Parent Object ** ~~~ ** Inlet Node :
> > HOUSEREHEATWATERINLETNODE ** ~~~ ** Outlet Node: HOUSEREHEATWATEROUTLETNODE
> >
> > I cannot understand why 'Inlet node did not find an appropriate matching
> > "outlet" node. Could someone tell me please how I should correct the
> > connection or send me an example if there is something available?
> >
> > Thanks,
> > K.
> >
> >
> > ---------------------------------
> > Yahoo! Mail is the world's favourite email. Don't settle for less, sign up for
> > your freeaccount today.
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
>
> ---------------------------------
> Yahoo! Answers - Get better answers from someone who knows. Tryit now.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/