Re: [EnergyPlus_Support] Understanding "Temp Rise Coefficient" input for Chiller:Electric module
Your description is correct.
Regarding the rated temperatures, the user specifies these, and must make sure
that all of the performance inputs form a consistent set, including the rated
temperatures. From the example object in the I/O Ref:
35.0, !- Temp Design Condenser Inlet {C}
2.778, !- Temp Rise Coefficient
6.67, !- Temp Design Evaporator Outlet {C}
So, in this example, the rated temperatures are 95F and 44F.
Mike
On 15 Aug 2007 at 7:58, Ian Doebber wrote:
> I do not understand what the inputs are for the "Temp Rise Coefficient" on page
> 412 of the InputOutputReference. For the example air cooled chiller idf, the
> value is 2.778. Therefore, the condenser difference (between Condesner
> Temperature Required to maintain rated capacity and the Rated Condenser Temp) is
> 2.778 time the evaporator difference (between Evap Temp Required and Rated Evap
> Temp).
>
>
>
> Are the rated temperatures based on the ARI National Standard of 95° F ambient
> and 44° F chilled water? If so, then what are the required temperatures based
> on?
>
>
>
> Ian Doebber
>
> Arup
>
> Mechanical Engineer
>
> Cell : 415-613-4314
>
> Fax : 415-957-9096
>
>
>
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup business
> systems are scanned for acceptability of content and viruses
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/