[EnergyPlus_Support] Re: Economics and Demand Cost Calculations



Thank you!

-Greg

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent" <brent_griffith@...> wrote:
>
> A formal methodology for splitting demand charges across end uses was
> prepared as part of the commercial building tax credits.  See section
> 3.1 of the report at:
> 
>  
> 
> http://www.nrel.gov/docs/fy07osti/40228.pdf
> 
>  
> 
> These calculations are not supported inside EnergyPlus; you would have
> to do them with postprocessing.
> 
>  
> 
> Input objects like the following can be used to report out the
> components of demand at the time they occur. 
> 
>  
> 
>    Report:Table:Monthly,
> 
>        Components of Peak Electrical Demand,  !- Name
> 
>        3,                        !- DigitsAfterDecimal
> 
>        Electricity:Facility,    !- VariableOrMeterName01
> 
>        Maximum,                 !- AggregationType01
> 
>        InteriorLights:Electricity,  !- VariableOrMeterName02
> 
>        ValueWhenMaxMin,         !- AggregationType02
> 
>        InteriorEquipment:Electricity,  !- VariableOrMeterName03
> 
>        ValueWhenMaxMin,         !- AggregationType03
> 
>        Fans:Electricity,        !- VariableOrMeterName04
> 
>        ValueWhenMaxMin,         !- AggregationType04
> 
>        Heating:Electricity,     !- VariableOrMeterName05
> 
>        ValueWhenMaxMin,         !- AggregationType05
> 
>        Cooling:Electricity,     !- VariableOrMeterName06
> 
>        ValueWhenMaxMin;         !- AggregationType06
> 
>  
> 
>  
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of boulder1259
> Sent: Friday, August 17, 2007 4:22 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: Economics and Demand Cost Calculations
> 
>  
> 
> What I am trying to do is figure out what portion of the utility bill is
> due to lighting, 
> HVAC, process, etc. (a common question from clients). The billing is
> simple: demand and 
> consumption charges. Since demand charges are by far the largest part of
> the bill, I 
> wanted an easy way to split these charges amongst the various services.
> If I understand 
> you correctly, this isn't possible with the current version of
> EnergyPlus.
> 
> Most of what you said about submetered charges not adding up to the
> facility metered 
> charges makes complete sense. My mistake was that I wasn't thinking
> about the 
> submeters as being actual meters. Any time demand charges are involved,
> I would expect 
> the sum of the submeters and facility meter to differ because the demand
> peaks on the 
> various meters are not likely not be coincident. Only if they were would
> I expect the two 
> to be the same.
> 
> Thanks,
> Greg
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> , "Michael J. Witte"
> <mjwitte@> wrote:
> >
> > I am not sure I understand what you are trying to do. The energy and
> demand 
> > charges within a given tariff will only be based on the specific meter
> or sub-
> > meter that is assigned to that tariff. If you want to calculate demand
> charges 
> > for the building as a whole but then separate energy charges by
> end-use, you 
> > would need a tariff connected to the facility electricity meter that
> calculates 
> > only demand charges, and then tariffs connected to submeters that only
> 
> > calcaulate energy charges.
> > 
> > Ultimately, I have to question your assumption that the submetered
> costs will 
> > add up to the same value as the facility meter costs. This will only
> be true 
> > if the rates are a very simple single charge for energy and for
> demand, say 
> > $0.10/kWh for energy and $15.00/kW for demand. If there are any sort
> of 
> > declining blocks or ratchets or other complexities to the rate
> structure, they 
> > will not total to the same value. The use of separate tariff objects
> in 
> > EnergyPlus is intended to be used when the building truly has meters
> which are 
> > separately billed, such as a separate meter for space-heating
> electricity.
> > 
> > Mike
> > 
> > 
> > On 13 Aug 2007 at 18:31, boulder1259 wrote:
> > 
> > > I'm trying to figure out a way to apportion various building service
> costs but
> > > am not having much luck.
> > > 
> > > When I sent up a tariff for facility-wide electricity charges (the
> charges
> > > include demand charges), EnergyPlus seems to produce reasonable
> values. 
> > > However, if I try to do the same for the various building services
> and then sum
> > > them, the sum of the charges does not match the value of when I look
> at the
> > > building as a whole.
> > > 
> > > I'm seeing that the electricity consumption charges can be summed,
> but that the
> > > electricity demand charges cannot. Apparently, the demand charges
> for the
> > > individual services (e.g., lighting) are not calculated from the
> facility's
> > > demand charges but rather independently.
> > > 
> > > Do you have suggestions of how to split the electric bill into its
> various parts
> > > (e.g., lighting, pumps, fans, etc.)?
> > > 
> > > Thanks,
> > > Greg
> > > 
> > > 
> > > 
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov <http://www.energyplus.gov> 
> > > 
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> <http://groups.yahoo.com/group/EnergyPlus_Support/> 
> > > 
> > > Attachments are not allowed -- please post any files to the
> appropriate folder
> > > in the Files area of the Support Web Site.
> > > 
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
> the
> > > Documentation link and press the "search" button.
> > > 
> > > Yahoo! Groups Links
> > > 
> > > 
> > > 
> > > 
> > >
> >
> 
>  
> 
> 
> 
> [Non-text portions of this message have been removed]
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/