[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] why enrgy consume always (almost) same for cooling and heating a whole year????



It is difficult to say, but it could be that the heating is actually
reheat.  (Because of humidity, cooling systems often need to overcool to
dry out the supply air and then reheat is used to avoid over cooling the
space.)  Unfortunately, in EnergyPlus it can be difficult to know what
part of the heating energy is actually being used for reheat.  One way
to tell is to look at when and why the heating and cooling is occurring
by reporting timestep frequency data for component energy use and air
node temperatures before and after the coils.  

 

 

 

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of
davistian_parmana
Sent: Tuesday, August 21, 2007 11:55 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] why enrgy consume always (almost) same for
cooling and heating a whole year????

 

hi,
i'm so confusing with my energy simulation results. 
i don't know why cooling energy consume not more bigger than heating
energy consume when summer season. it's also happened when winter
season, cooling energy rate always as big as heating energy rate. 
i don't know why,,,is scheduling caused this "weird" result???
so, should i turn-off cooling devices when winter season and turn-off
heating devices when summer season??? i don't know,,in Indonesia just
cooling a whole year,,,so i've no idea about it.thanks for your advices.

regards
-Davistian-

 



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/