That is very helpful and now makes sense! At what temperature and
pressure is the volumetric flow rate calculated? I get slightly
different values using STP conditions. How about documenting this and
modifying the .csv file to add the units in the description?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fred Buhl <wfbuhl@...> wrote:
>
> The "peak" value is the maximum of the individual timestep mass flow
> rates. It is in kg/s, as are
> the timestep numbers. The "Peak Vol Flow" is the peak converted to
> volumetric flow rate: its
> units are m3/s.
>
> Fred Buhl
>
> jvd2pe wrote:
> > When running a design-day-only simulation for the purpose of checking
> > zone sizing, the *****cZsz.csv file has the last two lines labelled
> > "Peak" and "Peak Vol Flow". For the mass flow rate columns, these
> > values differ, and the "Peak Vol Flow" value is always less than the
> > "Peak". What is the definition for these two values? (p.s., I have
> > NOT assigned a value for the "heating max air flow".)
> > Thanks in advance!
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/