Re: [EnergyPlus_Support] Starting simulation temperature
It is not a user-settable option. The warmup takes care of any
drifts caused by using that as starting temperature.
Search on "warmup" in the documentation for numerous mentions. In
the Building object:
Field: Loads convergence
This value represents the number at which the loads values must agree before
"convergence" is reached. (Units for this field is Watts.)
Field: Temperature Convergence
This value represents the number at which the zone temperatures must
agree (from previous
iteration) before "convergence" is reached. (Units for this field is delta C).
Convergence of the simultaneous heat balance/HVAC solution is reached
when either the
loads or temperature criterion is satisfied.
All tolerances have units so the temperature tolerance is in degrees
C (or degrees K) and the
loads tolerance is in Watts. Both tolerances work the same way, just
one looks at
temperatures and one looks at heating and cooling loads. After the
second warm-up day, the
program compares the maximum temperature experienced in a space with
the maximum
temperature from the previous day. If those two temperatures are
within the tolerance, then it
has passed the first warm-up check.
It does a similar comparison with lowest temperatures experience
within all the zones. If the
current simulation day and the previous day values are within the
tolerance, then it has
passed the second warm-up check. Similar things are done with the
loads tolerance and the
maximum heating and cooling loads that are experienced within the
spaces. Those are
compared individually to the values for the previous day. If they are
both in tolerance, then
the simulation has passed the third and fourth warm-up check. The
simulation stays in the
warm-up period until ALL FOUR checks have been passed.
Please note--other "convergence tolerance" inputs are required for
certain HVAC equipment
(unit ventilator, unit heater, window AC, etc.). The purpose and
units of these parameters are
different from "load convergence tolerance" and "temperature
convergence tolerance" in the
BUILDING object.
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/