Re: [EnergyPlus_Support] How do define a closed window and simulate a chimney
>From the ventilation expert . . .
For question 2: The AirflowNetwork is unable to model a chimney well. Your
anwser is correct. The main problem is that the relationship between pressure
and airflow is not well defined, although a crack component may be used when a
damper is close. The other problem is that no heat source is allowed in the
AirflowNetwork components.
For question 3: The AirflowNetwork model is unable to simulate single-side
ventilation well, because the model uses the same boundary conditions for
multiple openings at the same side. However, the model is able to handle cross
vent well.
On 31 Aug 2007 at 16:56, Michael J. Witte wrote:
> On 24 Aug 2007 at 19:04, raphmissah wrote:
>
> > 1. How to define a closed or partially opened window?
>
> EnergyPlus windows (Surface:HeatTransfer:Sub, Window) are always closed by
> default. To simulate opening of windows (partially or fully) for airflow, see
> the AirflowNetwork objects.
>
> > 2. How to simulate a chimney in a particular zone?
>
> One would use the AirflowNetwork multizone model to do this, but I am not sure a
> chimney can be modeled well. I will forward this to the natural ventilation
> experts.
>
> > 3. Lastly, a anything to learn on cross and single-sided ventilation?
> >
>
> I will ask the natural ventilation expert.
>
> Mike
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/