Re: [EnergyPlus_Support] Invalid Component name error



You used the zone name in the BRANCH instead of the unitary system 
object name.

And what is the second Compact HVAC:Zone:Unitary object shown below used 
for???

 Change the branch object to look like this:

BRANCH,
Branch_AirLoop_HP1, !- Branch Name
autosize, !- Maximum Branch Flow Rate {m3/s}
OUTSIDE AIR SYSTEM, !- Comp1 Type
OASystem_HP1, !- Comp1 Name
NodeIn_RA_HP1, !- Comp1 Inlet Node Name
NodeOut_MA_HP1, !- Comp1 Outlet Node Name
PASSIVE, !- Comp1 Branch Control Type
Compact HVAC:Zone:Unitary, !- Comp2 Type

 >>>> AHU_1, !- Comp2 Name

NodeOut_MA_HP1, !- Comp2 Inlet Node Name
NodeOut_SupplHtg_HP1, !- Comp2 Outlet Node Name
ACTIVE; !- Comp2 Branch Control Type


JV Dirkes II wrote:
>
> Dear E+ Support Group,
>
> I received the error message below, and cannot determine why
> "ZONE1_HP1" might be invalid. The only objects which use that name,
> other than Surfaces are also shown below.
>
> Your assistance will be appreciated!
>
> ** Severe ** During Branch Input, Invalid Component Name
> input=ZONE1_HP1
> ** ~~~ ** Component type=COMPACT HVAC:ZONE:UNITARY
> ** ~~~ ** Occurs on Branch=BRANCH_AIRLOOP_HP1
>
> BRANCH,
> Branch_AirLoop_HP1, !- Branch Name
> autosize, !- Maximum Branch Flow Rate {m3/s}
> OUTSIDE AIR SYSTEM, !- Comp1 Type
> OASystem_HP1, !- Comp1 Name
> NodeIn_RA_HP1, !- Comp1 Inlet Node Name
> NodeOut_MA_HP1, !- Comp1 Outlet Node Name
> PASSIVE, !- Comp1 Branch Control Type
> Compact HVAC:Zone:Unitary, !- Comp2 Type
> Zone1_HP1, !- Comp2 Name
> NodeOut_MA_HP1, !- Comp2 Inlet Node Name
> NodeOut_SupplHtg_HP1, !- Comp2 Outlet Node Name
> ACTIVE; !- Comp2 Branch Control Type
>
> ZONE,
> Zone1_HP1, !- Zone Name
>
> COMPACT HVAC:SYSTEM:UNITARY,
> AHU_1, !- Air Handling System Name
> Sch_Comp_HtgAvail_HP1, !- System Availability Schedule
> Zone1_HP1, !- Control Zone Name or Thermostat Location
>
> COMPACT HVAC:ZONE:UNITARY,
> Zone1_HP1, !- Zone Name
> AHU_1, !- Air Handling System Name
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/