Hi,

I am having difficulties understanding why the System Sizing routine 
limits the calculated system design air flow rate to a value lower 
than the user-input "Fixed" mimimum outside air flow rate, when the 
zone temperature is below the heating setpoint temperature. 
Lowering the supply heating air temperature resulted in even lower 
zone temperature without any changes to the calculated design flow 
rate. In a sizing calculation, I would expect a higher flow rate to 
be calculated to meet the setpoint temperature. Apparently i must be 
missing something! Please provide insight when possible. If you need 
a file to work with, use the IDF uploaded in the 
PROBLEM_SUBMITTAL\MAB3 folder on 10/10. Thank you for your support.

Merid 

P.S.
Calculated heating design air flow rates reported in the ".eio" file 
(under the System Sizing Information section)  are different that 
values listed in the ".CSV" file. Am I reading the reports wrong? 
Please verify if you have some time.



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/