Re: [EnergyPlus_Support] Window Opening Schedule



There are two approaches to modeling airflow from windows and doors.

The simple approach uses VENTILATION and INFILTRATION objects.

The more complex approach uses AIRFLOWNETWORK objects.  The specific object 
which controls window and door opening is AIRFLOWNETWORK:MULTIZONE:ZONE and/or  
AIRFLOWNETWORK:MULTIZONE:SURFACE.  Set "Ventilation Control Mode"=CONSTANT, and 
use the "Venting Availability Schedule Name" to control whether the opening 
(window or door) is open (sched value = 1) or closed (sched value = 0).  
"Window/Door Opening Factor, or Crack Factor" controls how much the window/door 
is opened.

Mike


On 31 Oct 2007 at 19:10, muhammadhaiderkhan wrote:

> i am trying to figure out how to put windows/doors to open and close
> on a schedule. 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/