Re: [EnergyPlus_Support] Door Opening Schedule
Haider:
When you use the AIRFLOWNETWORK:MULTIZONE:COMPONENT SIMPLE OPENING object as
an airflow component, the AirflowNetwork model calculates airflow across a
door opening component when a door is either open or close. Therefore,
although you specifies the door colse, the model still calculates the
airflow based on door-close conditions. It is expected to get different
results during winter time: no airflows from infiltration objects and
airflow from the door object. Please read the first paragraph under
AIRFLOWNETWORK:MULTIZONE:COMPONENT SIMPLE OPENING on page 639 in the Input
Output Reference.
Thanks.
Lixing Gu
----- Original Message -----
From: "muhammadhaiderkhan" <muhammadhaiderkhan@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Wednesday, November 14, 2007 11:40 AM
Subject: [EnergyPlus_Support] Door Opening Schedule
> Hi All,
>
> i am trying to simulate the opening and closing of door in commercial
> buildings during summer. i have tried using both the airflow network
> and the simple airflow object(infiltration). i have two identical IDF
> files, one setup such that the door remains closed year around and the
> other setup such that the door only open during 4 summer months.
>
> i am seeing unexpected results, as the hourly electricity and gas
> consumption in the hourly csv file (Filenamemeter.csv) shows a change
> in consumption between the two files during the winter months. i am
> thinking since the files are identical and the schedule is same during
> winter months the hourly consumption results should be identical, but
> that is not the case. does anyone have an idea why this would be?
>
> any thoughts would be much appreciated.
>
> thanks,
> Haider.
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/