Re: [EnergyPlus_Support] Can we use vertical insulation and under slab insulation together in slab.exe ?



The Slab program will model under slab insulation or vertical insulation, but 
not both together.

The presence of vertical insulation is controlled by the IVINS field in the 
Insulation object.  If this field is set to zero, then there is no vertical 
insulation.

Mike


On 21 Nov 2007 at 8:33, basill_xw wrote:

> Based on "AuxiliaryPrograms.pdf",If we choose under slab insulation
> configuration,R value of vertical insulation shoulb be zero.
> Does this mean the the vertical insulation and under slab insulation
> can't be in effect together?
> But there is the following words "the Depth of vertical insulation
> only should be .2 .4 .6 .8 1.0 1.5 2.0 2.5 or 3.0 m." 
> Does this mean the vertical insulation will always exist in slab.exe?
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/