Re: [EnergyPlus_Support] Re: convection coefficient



No, you can specify the exact surface that you want to apply the 
convection coefficients to -- unless you want to do all exterior windows.

For example, if you wanted to set convection coefficients for a surface:
  CONVECTIONCOEFFICIENTS,
          ZONE SURFACE SOUTH,
          Interior,
          Value,
          3.076,
          ,
          Exterior,
          Value,
          10.22,
          ;

When you are doing more than one surface you would use:
   CONVECTIONCOEFFICIENTS:MULTIPLESURFACE,
     AllExteriorWindows,      !- SurfaceTypes
     Exterior,                !- Convection Type #1
     MoWitt;                  !- Convection Value Type #1


At 12:47 PM 11/30/2007, anca_unica wrote:
>What should I use for the thermal
>resistance between the glass and for the shade?

I don't know -- you might look at the example file
AirflowWindowsAndBetweenGlassShades.idf

for some ideas.


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/