EnergyPlus initializes each simulation environment (design day or weather file 
run period) by repeating the first day of the environment until the results 
converge, then the simulation proceeds with the next day.  If you look at the 
results for 07/15 hour 24, they are very similar to the results reported in the 
first row for 07/15 hour 0.  So this looks quite reasonable.  This trend 
repeats itself each night around midnight in the following days.  "Opaque 
Surface Inside Face Conduction" is the only variable being reported here.  
Because this variable represents the net result of many factors, it can be 
difficult to understand the driving forces.  I would recommend reporting some 
environmental conditions and zone air temperatures at a minimum to help 
understand what it happening.

Of greater concern are the 14C ground temperatures year-round.  These are much 
too cold under a commercial building.  The floor surfaces in contact with the 
ground are drawing significant amounts of heat from the building. Please read 
about ground temperatures in the Auxiliary Programs document.

Mike


On 29 Nov 2007 at 1:43, Àî ×¼ wrote:

> Thank you for your answer.
> I have already uploaded the IDF.
> I am simulating a three floor builing in this E+ work.
> There are totally fifteen zones in the building.The object with "-1-
> " means it is in the first floor,and "-3-" means it is in the third 
> floor,The one have a name with no number is the second floor object.
> The weather data I used is CHN_ChangSha_CSWD.epw.I also uploaded 
> this EPW. 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad 
> <RRaustad@...> wrote:
> >
> > We will need your input file for further investigation. Please 
> upload 
> > your file to the EnergyPlus Support group in the Files area using 
> the 
> > Problem Submittals folder..
> > 
> > Àî ×¼ wrote:
> > >
> > > Dear Richard,
> > > Thank you for your attention.
> > > This is a example.These numbers are from my E+ work CSV report 
> file
> > > and they represent Opaque Surface Inside Face Conduction for some
> > > patition walls.The zones are cooled by Purchased Air and the
> > > temperature setpoit is 26C.Only the numbers in the first line 
> seem
> > > to be bad values.
> > > 00:10:00,-55,-105,-53,-227, 56, -165, -17, -7
> > > 00:20:00,60, 36, 63,-83, 185, 12, 45, 55
> > > 00:30:00,60, 37, 63,133, 146, 18, 46, 57
> > > 00:40:00,58, 34, 60,141, 138, 16, 45, 56
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > <RRaustad@> wrote:
> > > >
> > > > You will have to provide more information. What report 
> variables
> > > do
> > > > these numbers represent? Can you open the csv in a text editor 
> and
> > > > cut-and-paste in the first 2 lines? Right-click on the file and
> > > select
> > > > Open With/WordPad (or any text editor). Or open WordPad and 
> then
> > > select
> > > > File/Open and pick the csv. Then cut-and-paste.
> > > >
> > > > Àî ×¼ wrote:
> > > > >
> > > > > Hello,everyone
> > > > > I fined that the numbers in the first row of the CSV report 
> file
> > > seems
> > > > > to be bad values in my E+ works.Can you tell me the reason?
> Than
> > > you
> > > > > very much.
> > > > > For example:
> > > > > 1stRow Number -55.63142475 -227.006426
> > > > > follow-up 36.69246574 -83.86553404
> > > > > 37.52008086 -133.0062585
> > > > > 34.18661976 -141.388429
> > > > >
> > > > >
> > > > >
> > > > >
> > > > >
> > > > >
> > > >
> > > > --
> > > > Richard A. Raustad
> > > > Senior Research Engineer
> > > > Florida Solar Energy Center
> > > > University of Central Florida
> > > > 1679 Clearlake Road
> > > > Cocoa, FL 32922-5703
> > > > Phone: (321) 638-1454
> > > > Fax: (321) 638-1439 or 1010
> > > > Visit our web site at: http://www.fsec.ucf.edu 
> <http://www.fsec.ucf.edu>
> > > >
> > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > >
> > >
> > >  
> > 
> > -- 
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL  32922-5703
> > Phone:   (321) 638-1454
> > Fax:     (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> > 
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/