[EnergyPlus_Support] Re: HELP!! - EnergyPlus crash



You can change the input file as follows,

1: change the sequence of splitter and mixer of 8 connectors in the
"connector list". Firstly specify splitter, Secondly mixer. Then
warning and severe errors appear in the err file. 
2: There are errors in the heating demand and supply splitter and
mixer. In the object of splitter, change the name of "HEATING DEMAND
(or SUPPLY) MIXER " into "HEATING SUPPLY (or DEMAND) MIXER". In the
object of mixer, please do the same. 
3: In the "WATER SYSTEM DEMAND MIXER", change the outlet branch name
from "Heating Demand Outlet Branch" to "Water System Demand Inlet Branch".
4: For chiller and boiler, coefficients of these equipments are required.
5: During Plant ( Condenser) Equipment List Input, correct the errors
of component type. 
6:In the "Condenser loop", you confused the supply loop with demand loop. 
7: Specify the condenser loop temperature set-point. 
There are still some errors about "Node Connection Error". 

I hope it helps.

Tj Ywh


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "brandao_nuno"
<ncostab@...> wrote:
>
> Dear Support Group,
> 
> I´m studying the 5ZoneWaterSystems.idf example file. As an exercise, I
> tried to redo the example file from the beginning. After correcting
> some node syntax errors, the simulation suddenly crashed. I tried
> pausing the simulation but i´m not able to find the exact error
location. 
> I´m uploading the idf file so that you can have a look at it.
> 
> Thanks in advance
> Nuno Brandao
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/