Re: [EnergyPlus_Support] Re: ATUs - Insufflated vs. Exhaust Air flows
Cross mixing simply exchanges and equal amount of air between two zones. It is
a zone heat balance function and the air handling system knows nothing of it.
On 11 Jan 2008 at 17:52, anarui.oliveira wrote:
> Thanks a lot for all your answers.
>
> Regarding option 4:
> - If I use Cross-mixing instead, doesn't the program account for the
> corresponding outgoing flow in the source zone?
>
> Thanks again,
> Ana Rui.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@...> wrote:
> >
> > 1. First, I will clarify some terminology:
> > Return air flow - air leaving the zone and returning to the HVAC
> system
> >
> > Exhaust air flow - air leaving the zone and exhausted to outdoors
> >
> > Return air flow rate is computed as Supply air flow minus Exhast
> air flow
> >
> > I am not sure when you say "exhaust" if you mean return or exahust
> as defined
> > above. I will use my definitions below.
> >
> > 2. The systems created by Compact HVAC assume that return air flow
> is equal to
> > supply air flow.
> >
> > 3. If you want to add exhaust air flow, you can add ZONE EXHAUST
> FAN objects by
> > editing the expidf file.
> >
> > 4. If you want to model a constant (or scheduled) flow from one
> zone to
> > another, you can use a MIXING object to move air from one zone to
> another.
> > However, the HVAC system has no knowledge of this and the user must
> balance the
> > airflows by adding a dummy ZONE EXHAUST FAN to the source zone to
> cause a
> > reduction in return air flow from the source zone.
> >
> > 5. For constant volume systems, you can use
> AIRFLOWNETWORK:DISTRIBUTION:*
> > objects to model the pressure-indcued flows, but this feature does
> not yet
> > support VAV systems.
> >
> > Mike
> >
> >
> > On 9 Jan 2008 at 16:23, anarui.oliveira wrote:
> >
> > > Hi.
> > >
> > > The parameters for ATU, such as those cretated by
> > > - Compact HVAC:Zone:VAV,
> > > - Compact HVAC:System:VAV,
> > > only allow the user to define the insufflated air flows (Supply
> air
> > > flow), right?
> > >
> > > What does the simulation assume, in this case, for the exhaust
> air
> > > flows, and how does it deal with the corresponding effect on the
> > > inside pressures?
> > >
> > > If the case to model has different insufflated and exhaust flows,
> how
> > > does it affect my model? Wow can I implement this in E+?
> > >
> > > And if a certain zone only has forced exhaust flow, and the inlet
> > > flow is assumed to be drawn from adjacent areas by pressure
> > > difference?
> > >
> > > Thanks in advanced.
> > >
> > > Best regards,
> > > Ana Rui.
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> appropriate folder
> > > in the Files area of the Support Web Site.
> > >
> > > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
> under the
> > > Documentation link and press the "search" button.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@...
> >
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/