If the zone temperature is held at the same temperature in both cases, 
compare the zone humidity levels. You will probably find that the DX 
Coil maintains a lower zone humidity level which would probably account 
for the difference in cooling energy..You could also compare the 
humidity ratio of the supply air for each system. Does the DX Coil 
provide a lower humidity ratio? You could also report the supply air 
mass flow rate and enthalpy and calculate the delivered cooling energy 
as a check.

anarui.oliveira wrote:
>
> Hello all.
>
> If (for cooling only), maintaining all other parameters in a model:
>
> - a PTAC is fully set to autosize, and a simulation is run,
> - and then it is substituted by a simple Purchased Air configuration,
> for the exact same zone and thermostat,
>
> why is the "DX Coil Total Cooling Energy" between 1.5 to 4 times higher
> than the "Purchased Air Total Cooling Energy"?
>
> I know "Purchased Air" is a simplification, but since we're looking
> directly at the thermal loads, and not any efficiency-dependent
> consumption variable, where does this difference come from?
>
> Regards,
> Ana Rui.
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/