[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: How to control the outdoor air rate and total air flow rate in the HVAC system?



1. Yes
2. Yes.  

On 13 Jan 2008 at 22:36, jpei82 wrote:

> Thank you so much for your reply! Now I have some questions, :)
> 
> 1. If constant volume system is used, the OA flow and the primary 
> loop air flow rate will be constant as designed, right?
> 
> 2.if I still use VAV system, but change the VAV terminal unit min 
> flow fraction to 1, and set the primary loop flow rate, then the sum 
> of zone flow rate will be the primary loop flow rate, am I correct?
> 3. if 2) is correct, the real OA flow will be the same as set in zone 
> sizing. is that true? 
> 
> Since I am a beginner of EnergyPlus, Thank you so much again for 
> patience!
> 
> Jingjing
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> <mjwitte@...> wrote:
> >
> > The values in zone sizing objects and the desing flow rates will 
> occur when the 
> > system is running a full flow.  For a VAV system, this will not 
> occur very 
> > often - only on the hottest days and during recovery from setback.
> > 
> > For VAV systems, the outside air flow rate can be proportional to 
> the system 
> > flow rate (which means the outside air fraction remains constant), 
> or a fixed 
> > amount (which means the outside air fraction varies).  See 
> CONTROLLER:OUTSIDE 
> > AIR for more details.  But note that the VAV terminal unit min flow 
> fractions 
> > must be consistent with the OA requirement.  If the total system 
> supply air 
> > flow falls below the min OA requirement, the OA flow will also 
> drop, even when 
> > using the fixed amount OA control.
> > 
> > Mike
> > 
> > 
> > On 9 Jan 2008 at 23:20, jpei82 wrote:
> > 
> > > Hi, all, now I want to simulate the energy consumption difference 
> > > between different ourdoor air flow rate. I specify the required 
> OA flow 
> > > rate in "zone sizing" by "outside air flow per zone", but found 
> that 
> > > the "zone mechanical ventilation volume flow rate" in the result 
> does 
> > > not agree with the value I specified. what is the reason? 
> > > 
> > > Also , I give a fixed value in "design air flow rate" 
> for "primary air 
> > > loop"  , but the volume flow rate for "mixed air node" (also VAV 
> sys 
> > > inlet node, VAV sys outlet node, they have the same value), is 
> not the 
> > > value I gave, but much smaller. I supposed they should be the 
> same. Can 
> > > anyone tell me the reason? Thanks a lot!
> > > 
> > > 
> > > 
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > > 
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > 
> > > Attachments are not allowed -- please post any files to the 
> appropriate folder
> > > in the Files area of the Support Web Site.
> > > 
> > > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
> under the
> > > Documentation link and press the "search" button.
> > > 
> > > Yahoo! Groups Links
> > > 
> > > 
> > > 
> > > 
> > > 
> > 
> > 
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support      
> > EnergyPlus-Support@...
> >
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 






The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/