Right.
I switched the pump operation to intermittent and it doesn't happen
any more.
Maybe I only noticed it after adding the internal gains because the
overall temperatures became higher(?); I checked and it also happened
before adding the internal gains, although the temperatures didn't
rise so much.
Thanks.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> My guess is that the hot water loop pump is running continuously
and adding
> pump heat to the loop. Check the pump controls on the chilled
water loop, it
> may also be running continuosly, but in the chilled water loop, the
chiller
> will come on to offset the pump heat. You may wish to schedule the
pump
> operation or change it to intermittent for both loops.
>
> Mike
>
>
> On 14 Jan 2008 at 18:34, anarui.oliveira wrote:
>
> > When I add internal gains to may model, (which as a chilled and a
hot
> > water loop, served by chiller and boiler, respectively), the
> > Temperatures at the inlet and outlet of the hot water loop (and
> > boiler), in a summer week, when the boiler is off (I checked!)
start
> > rising steadily, well above the nominal boiler temperature and
the zone
> > temperatures (even those of the uncontrolled zones).
> > NO similar effect occurs in the chilled water loop, nor in the
winter
> > nor in the summer.
> > I can't see the relationship behind this effect and I'm worried
it
> > reveals some problem with the modelling.
> > Can anyone help me?
> >
> > Thank you,
> > Ana Rui
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/