RE: [EnergyPlus_Support] very very hard question
Those masses are not included in that air mass term and are not "assumed
to be in equilibrium with the zone air." Their heat balance impact
enters in the hA(T - T) term.
Internal thermal mass is entered with the
Surface:HeatTransfer:InternalMass input object and is treated like a
surface that interacts with zone air much like a normal heat transfer
surface. There is surface convection and thermal radiation with other
surfaces. They have heat capacity and are modeled dynamically.
(If one really did need to control heat capacity of zone air, it can be
done with the Zone Volume Capacitance Multiplier input object. )
________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of anca_unica
Sent: Friday, January 18, 2008 5:25 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] very very hard question
Hi all
I'm trying to understand from EnergyPlus Engineering Document which is
the energy balance equation used by the software.
Pag 5: Typically, the capacitance Cz would be that of the zone air
only. However, thermal masses assumed to be in equilibrium with the
zone air could be included in this term.
How it calculates the Cz value including thermal masses?
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/