Re: [EnergyPlus_Support] settings etc. about chilled water pump power per flowrate



1.  In the pump object, the pressure rise and efficiency inputs control the 
power consumption.

2.  PLANT SIZING

3.  I am not exactly sure about this, but see CONDENSER LOOP, field "Loop 
Temperature Setpoint Node Name or Reference".  If you enter AIR in this field, 
then "use the outdoor air wet-bulb as the setpoint".  Input Output Reference p. 
393, pdf p. 434.

Mike




On 17 Jan 2008 at 9:19, eric_zhou1223 wrote:

> Hi all,
> 
> I have some questions for a LEED project and need confirmation:
> 
> 1. how can the "chilled water pump power per flowrate" be define?
> 2. Where can I set the "chilled/hot water loop temperature rise/drop"?
> 3. can the axial fan in the cooling tower be defined with wetbulb reset 
> control?
> 
> Your help would be much appreciated.
> 
> Eric
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/