Re: [EnergyPlus_Support] VAV: Reheat coil vs. Baseboard heating



The reheat coil requires air flow from the central air loop or from a powered 
induction unit.  Baseboard heat uses natural convection.  A heating coil object 
is not necessary for baseboard, the baseboard object is the "coil".  You may 
find it helpful to create two input files, one with baseboard and one with 
reheat, and then compare the expidf output files to see the differences.

Mike


On 25 Jan 2008 at 17:52, anarui.oliveira wrote:

> Hi.
> 
> Can anyone tell me:
> 
> - When creating a Compact HVAC: Zone: VAV, what are the essential 
> differences between:
>   - Reheat Coil: Hot Water
> and
>   - Baseboard Heating: Hot Water
> They will both require specification of a Heating coil, right?
> 
> Thanks in advance,
> Ana Rui.
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/